phase convertor
« on: August 16, 2015, 02:51:13 PM »
third project that I completed was my 4kW phase convertor.  Originally I had a small static one but with the larger mill it would not cut it.  This design wasw based on the info from the workshop practice series 'three phase conversion'.

The step up transformer is a modified cytringan 180A stick welder, that also still serves as my AC stick welder(£30 ebay)



The idler motor is a 4kW unit from ebay (£40).  This picture shows it running unloaded, the voltages are better matched with some load:


Gubbins - main contactor, idler thermal trip, driven equipment thermal trip, start capacitors and relay as well as run capacitors:



Works well, runs larger equipment than the static machine does and smaller equipment more smoothly that the old static.  At about £120 all in was much cheaper than putting an invertor on all mu machines, although clearly you have no ability to change speed.

Offline rotorhead

  • Full Member
  • ***
  • Posts: 165
  • Country: england
Re: phase convertor
« Reply #1 on: August 19, 2015, 05:16:29 PM »
Impressive to say the least, I had to go with what's on offer, ready made wise, as I haven't a clue when it comes to electronics...well done...
Chris
Sunny Scunny,
North Lincolnshire.

Offline Auskart

  • Jr. Member
  • **
  • Posts: 20
  • Country: au
Re: phase convertor
« Reply #2 on: August 20, 2015, 02:58:59 AM »
Do you have a circuit diagram for it.

Cheers Shane.

Offline Andrew Wildman

  • Full Member
  • ***
  • Posts: 167
  • Country: 00
Re: phase convertor
« Reply #3 on: August 20, 2015, 07:51:13 AM »
hi shane,
If you are interested in building one it is worth buying the book that I referenced as it gives a lot of other useful info.  The circuit diagram can be made up from bits of the book

Offline glumpy

  • Jr. Member
  • **
  • Posts: 8
  • Country: au
Re: phase convertor
« Reply #4 on: August 25, 2015, 10:54:55 PM »

The couple of things that I have that are 3 phase I just set up individually.  That way you can fine tune each machine to get the best performance.
It's just some caps that I start off with some ballpark values for and test from there till I get the best start and run.

Clearly you must have some professional electric education to wire something like your converter  up. It's a real beauty and so neatly laid out.
I'd be putting a clear cover on the thing and lying I lost the original one just so I could show off my handy work to my mates and -appear- to be humble about it!  :0)

Offline DavidA

  • Hero Member
  • *****
  • Posts: 1219
  • Country: gb
Re: phase convertor
« Reply #5 on: August 30, 2015, 02:28:17 PM »
Andrew,

Very interesting. It may be the way for me to go.

One small point, very small,  usually three phase wiring is red, white (or yellow) and blue.
Is there any particular reason you chose black, brown and grey. ?

Just curious.

Dave.

Offline John Rudd

  • Hero Member
  • *****
  • Posts: 2525
  • Country: gb
Re: phase convertor
« Reply #6 on: August 30, 2015, 02:37:44 PM »
BBG are the European harmonised colours for wiring 3 phase ..... :zap:

Admittedly I prefer the RYB scheme, much more colorfulcolourful..... :lol:
eccentric millionaire financed by 'er indoors
Location:  Backworth Newcastle

Skype: chippiejnr

Offline vtsteam

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 6466
  • Country: us
  • Republic of Vermont
Re: phase convertor
« Reply #7 on: August 30, 2015, 08:16:49 PM »
Very nice installation!  :thumbup: :clap:
I love it when a Plan B comes together!
Steve
https://www.youtube.com/watch?v=4sDubB0-REg

Offline rotorhead

  • Full Member
  • ***
  • Posts: 165
  • Country: england
Re: phase convertor
« Reply #8 on: September 01, 2015, 12:31:05 AM »
Hi Lads,

Bought some 3+E cable from a wholesaler a bit back, the colouring of that cable confused me too as it was Brown, Black, Grey and earth(Green)...
Chris
Sunny Scunny,
North Lincolnshire.

Offline DavidA

  • Hero Member
  • *****
  • Posts: 1219
  • Country: gb
Re: phase convertor
« Reply #9 on: September 01, 2015, 12:30:27 PM »
Yes, Makes you wonder why there was a need to change from the Red, Yellow and blue.

I'm certain that the old system was easier to differentiate in bad lighting conditions.

Anyway, I've sent for the book and it will probably be placed on the 'things to do' list.

Andrew,

Was there any thing not mentioned in the book that needs to be known ?

Dave.

Offline bertie_bassett

  • Full Member
  • ***
  • Posts: 179
  • Country: 00
Re: phase convertor
« Reply #10 on: September 01, 2015, 05:57:35 PM »
Hi Lads,

Bought some 3+E cable from a wholesaler a bit back, the colouring of that cable confused me too as it was Brown, Black, Grey and earth(Green)...

just wait till you get a 5 core (3+N+E) that now got the blue in it for the neutral. connect it up to an older install with old colours ( blue for L3 and black for N) and your in for a right bit of confusion!

a competent engineer uses the tools and knowledge available, to get a challenging job done.

 An incompetent "engineer" tells his boss that the existing equipment "can't do the job" and to get another machine

Offline Andrew Wildman

  • Full Member
  • ***
  • Posts: 167
  • Country: 00
Re: phase convertor
« Reply #11 on: September 02, 2015, 08:01:29 AM »
Dave, the book is pretty good.  Using the welder as the autotransformer was my idea and wiring in the volt meters was also not in the book but the book covers the rest.  there is a bit of pulling together various bits that are scattered through the book to suit your installation but it is not too difficult.

Offline DavidA

  • Hero Member
  • *****
  • Posts: 1219
  • Country: gb
Re: phase convertor
« Reply #12 on: September 02, 2015, 09:54:47 AM »
Andrew,

Thanks. The book should be here in the next couple of days and I am looking forward to planning the project.
I've a pretty good idea of what will be involved (I was an apprentice industrial electrician many years ago, before I switched to Diesel mechanic) and don't see any big problems.

The voltmeters to monitor each phase is a good idea. I may steal it.

Dave.

Offline Andrew Wildman

  • Full Member
  • ***
  • Posts: 167
  • Country: 00
Re: phase convertor
« Reply #13 on: September 02, 2015, 02:30:57 PM »
look forward to seeing your progress.  The voltmeters are just ebay cheepos but they are sufficient to ensure that the voltages are fairly balanced and to ensure that you are getting 3 phase.

lordedmond

  • Guest
Re: phase convertor
« Reply #14 on: September 02, 2015, 02:38:25 PM »
When I started my apprenticeship  TP colours were Red White and Blue   neutral was Black earth was Green

a couple of years later White became Yellow

but as has been said the old colours were better in low light and dirty conditions

TRS was mucky Red, mucky Black and evan more mucky Green , get some founder dust on them and a bell set was your friend

personally I do not like the new style TP&N colours


Stuart

Offline DavidA

  • Hero Member
  • *****
  • Posts: 1219
  • Country: gb
Re: phase convertor
« Reply #15 on: September 02, 2015, 02:59:42 PM »
I understand that one justification for the change was that colour blind people have problems with red and green.

Dave.

lordedmond

  • Guest
Re: phase convertor
« Reply #16 on: September 02, 2015, 03:14:24 PM »
Yep one of the electricians I worked with during my time was colour blind on red and green , it was the old TRS cable that he had trouble with especially in the moulding shops

CB is common in males but uncommon in females , my daughter is CB on R and G , but I am ok and there is no history in mine or the wife's family .



To the OP sorry to derail your thread you did a good job on the phase converter , what's the PF like , do the caps provide enough lead to counteract all the inductance in the circuit with two motors running

Stuart

Offline DavidA

  • Hero Member
  • *****
  • Posts: 1219
  • Country: gb
Re: phase convertor
« Reply #17 on: September 04, 2015, 05:52:35 AM »
Andrew,

The book arrived yesterday and I had a quick scan of the relevant parts.

It appears that the heart of the whole thing is the 240 to 415 Volt auto transformer conversion.
The rest being a normal Steinmetz capacitor arrangement driving an idler motor.
So I don't anticipate too many problems.
I've done a couple of transformer rewinds in the past and found the most difficult part getting the lamination's back in place.
Now need to go have a good look at my old stick welding set.

Dave.

Offline Andrew Wildman

  • Full Member
  • ***
  • Posts: 167
  • Country: 00
Re: phase convertor
« Reply #18 on: September 04, 2015, 07:37:26 AM »
dave,
I did not rewind my welder.  I looked specifically for a 240/415 v input version and then just connected 240 in and 415 out (built a little terminal box that sits on the top plate) also means it still works as a welder  :zap:

Offline DavidA

  • Hero Member
  • *****
  • Posts: 1219
  • Country: gb
Re: phase convertor
« Reply #19 on: September 04, 2015, 09:26:06 AM »
Andrew,

That's cheating; but a good idea.

I may look around for a dual voltage welder on ebay and sell my present single voltage one.

Lot's of options.

Dave.

Offline John Rudd

  • Hero Member
  • *****
  • Posts: 2525
  • Country: gb
Re: phase convertor
« Reply #20 on: September 04, 2015, 10:17:08 AM »
Dave
It may be worth considering buying a transformer if you have the money....
Try Drives Direct and ask for Dave..
No affiliation etc.....
eccentric millionaire financed by 'er indoors
Location:  Backworth Newcastle

Skype: chippiejnr

Offline DavidA

  • Hero Member
  • *****
  • Posts: 1219
  • Country: gb
Re: phase convertor
« Reply #21 on: September 04, 2015, 02:05:15 PM »
 John R,

Thanks for the tip.  I'll do that.

Dave :thumbup:

Offline DavidA

  • Hero Member
  • *****
  • Posts: 1219
  • Country: gb
Re: phase convertor
« Reply #22 on: September 08, 2015, 09:45:37 AM »
John R,

Successful outcome with Drives Direct. Transformer arrives Thursday.

Thanks again for the tip.

Dave.

Offline Thomas Webb

  • Newbie
  • *
  • Posts: 1
Re: phase convertor
« Reply #23 on: September 12, 2015, 01:36:19 PM »
Hello Andrew, I have a welder it is 440v or 240v (89 and 100v)input Will it be ok to step up on rotary converter?

Offline Andrew Wildman

  • Full Member
  • ***
  • Posts: 167
  • Country: 00
Re: phase convertor
« Reply #24 on: September 13, 2015, 05:09:23 PM »
Thomas, that will probably be a bit high as the voltage I get is higher than the 415 tapping of the transformer if the load is not optimum for the caps that I used. Also will require 500v caps which you may find hgarder to get hold of.

Offline Andrew Wildman

  • Full Member
  • ***
  • Posts: 167
  • Country: 00
Re: phase convertor
« Reply #25 on: September 13, 2015, 05:11:34 PM »
Dave, if you don't mind me asking, how many quid was the transformer?

Offline DavidA

  • Hero Member
  • *****
  • Posts: 1219
  • Country: gb
Re: phase convertor
« Reply #26 on: September 14, 2015, 07:45:46 AM »
Andrew,

No problem.  It was £225 + £15 carriage.

Quite expensive for a transformer, But now I have it it should be very versatile.

I did notice something about it that I didn't expect. But I'll come back on that when I have done a few measurements.

Dave.

Offline DavidA

  • Hero Member
  • *****
  • Posts: 1219
  • Country: gb
Re: phase convertor
« Reply #27 on: September 14, 2015, 07:51:33 AM »
Thomas,

Andrew wrote,

.. Also will require 500v caps which you may find hgarder to get hold of...

This is true.  But you can always put two or more capacitors in series and this will increase the working voltage. But it will reduce the capacitance.

So two 250 volt 10 MicroFarad capacitors in series will give you a working voltage of 500 Volt. But an overall capacitance of only 5 Microfarad.

It means more capacitors are needed, but it does work.

Dave.

Offline John Rudd

  • Hero Member
  • *****
  • Posts: 2525
  • Country: gb
Re: phase convertor
« Reply #28 on: September 14, 2015, 09:04:32 AM »
And.....dont forget to fit bleeder resistors across them all..... :zap:

Id like to think I can sell you something else of use to you....... :lol:

More seriously, caps exploding isnt funny, Ive had it happen to me, apart from the mess ( of the cap that is.... ) my nerves arent up to it anymore..... ( runs and hides ....)

Id sure like to hear when its finished and how it performs....

What rating are you aiming for Dave?
eccentric millionaire financed by 'er indoors
Location:  Backworth Newcastle

Skype: chippiejnr

Offline DavidA

  • Hero Member
  • *****
  • Posts: 1219
  • Country: gb
Re: phase convertor
« Reply #29 on: September 14, 2015, 01:45:01 PM »
Joun,

Don't worry, I wont forget the resisters on my set up.

The transformer is a 4 KWatt model.

I'll probably aim at a rating of 1.5 KWatt (to match your motor if I use it as an idler), otherwise it will be rated to the largest motor I have. That would be my Denford lathe at 1.2 KWatt.

With the 240 to 415 Volt transformer I could just use the Steinmetz capacitor set up to derive the artificial phase and leave it at that. But using an idler (Ok, I know it really should be about 2.5 KWatt, but it is only on a low duty) I hope to get a better start up. The chuck is quite heavy.

Anyway we will see.

The motor on my Emco milling attachment is less than 1 KWatt. I have a big drilling machine but the motor on that is only 0,5 KWatt.

So it should all work.

I need to find my AVO and take measurements. Then do some calculating.

Maybe need to build a switched bank of capacitors.

Dave.

Offline DavidA

  • Hero Member
  • *****
  • Posts: 1219
  • Country: gb
Re: phase convertor
« Reply #30 on: November 01, 2015, 01:40:57 PM »
A progress report; sort of.

I have been waiting for the arrival of a capacitance meter to find out what the value of the capacitors I have actually is as against what it says on the can.

The calculated value required is 4.16 MFD.

My nominal 7.5 MFD unit measured at 6.7 MFD.  Near enough for a test. I'm expecting a high voltage because of this.

So, being a believer in checking the system in it's constituent parts as it is being assembled, I decided to find out what Voltage I was getting form the new auto transformer.

A kettle lead was to hand so the kettle end was cut off and the wires connected to the transformer 220 Volt primary.  Switched on .

And the lights went out.

The RCD in the house had tripped.

Further examination revealed there was a leak between the live and the earth inside the molded plug on the lead.

A new plug was fitted.  Power on.

A gentle hum from the transformer.

Measured 220 Volt at the primary and 415 at the secondary terminal.

So far so good.

I then connected up capacitor and the three phase leads to the Milling attachment.

Now, I'm not sure if I should get the full artificial phase voltage when the motor isn't running. But I measure only 163 Volt across it on the input side of the stop/start switch.

Pressed the start button.  Nothing happened. No comforting 'clack' of the contactor slamming in.

I have to state that I have never seen this attachment running. So it is quite possible that there is a problem with it or the switch.

Called it off for the night. Further investigations tomorrow or Tuesday.
I think I will use the new motor I bought as I know it should work. Then come back to the mill.

Dave.

Offline John Rudd

  • Hero Member
  • *****
  • Posts: 2525
  • Country: gb
Re: phase convertor
« Reply #31 on: November 01, 2015, 01:51:53 PM »
A progress report; sort of.

I think I will use the new motor I bought as I know it should work.
Dave.

Of course it will work, think positive...( no pun intended.... :lol: )
eccentric millionaire financed by 'er indoors
Location:  Backworth Newcastle

Skype: chippiejnr

Offline DavidA

  • Hero Member
  • *****
  • Posts: 1219
  • Country: gb
Re: phase convertor
« Reply #32 on: November 01, 2015, 02:10:08 PM »
John,

I have every confidence in the motor.

But there again, I had every confidence in the kettle lead.

Dave. :scratch:

Offline vintageandclassicrepairs

  • Full Member
  • ***
  • Posts: 218
Re: phase convertor
« Reply #33 on: November 01, 2015, 02:20:42 PM »
Hi,
Quote
Now, I'm not sure if I should get the full artificial phase voltage when the motor isn't running. But I measure only 163 Volt across it on the input side of the stop/start switch.

Pressed the start button.  Nothing happened. No comforting 'clack' of the contactor slamming in.

You need to use the "real" phases for the control circuit, ie. the output phases from the transformer if the controls are 415v

HTH
John

Offline DavidA

  • Hero Member
  • *****
  • Posts: 1219
  • Country: gb
Re: phase convertor
« Reply #34 on: November 01, 2015, 02:26:14 PM »
John,

Thanks. I wondered about that but didn't want to get involved with it tonight. It does make sense.
I'll check tomorrow to see which phase is feeding the solenoid. It is a 415 Volt control.

Dave

Offline DMIOM

  • Hero Member
  • *****
  • Posts: 676
  • Country: gb
  • Isle of Man
Re: phase convertor
« Reply #35 on: November 01, 2015, 06:44:34 PM »
A progress report; sort of.

I have been waiting for the arrival of a capacitance meter to find out what the value of the capacitors I have actually is as against what it says on the can.

The calculated value required is 4.16 MFD.

My nominal 7.5 MFD unit measured at 6.7 MFD.  Near enough for a test. I'm expecting a high voltage because of this.

...........

Not surprised if your caps are Mega Farads....  :scratch:

Offline Bluechip

  • Madmodder Committee
  • Hero Member
  • *****
  • Posts: 1513
  • Country: england
  • Derbyshire UK
Re: phase convertor
« Reply #36 on: November 02, 2015, 03:58:39 AM »


Not surprised if your caps are Mega Farads....  :scratch:

 :lol:  :lol:  :lol:

Dave
I have a few modest talents. Knowing what I'm doing isn't one of them.

Offline DavidA

  • Hero Member
  • *****
  • Posts: 1219
  • Country: gb
Re: phase convertor
« Reply #37 on: November 02, 2015, 07:45:12 AM »
DMIOM,

...Not surprised if your caps are Mega Farads....

If you go to the following site..

https://en.wikipedia.org/wiki/MFD

and look at the third item in the section on science, technology and medicine,  you will find that MFD is the old abbreviation for MicroFarad; which was the way I intended it to be understood. Old habits die hard.

I understand that humble pie is best served with a chilli sauce.

I didn't use the Mu character as I don't know how to get it.

Anyway, onwards.

It dawned on me last night that the best way to go would be to first connect the motor directly to the three phase supply, by-passing the contacter.

Upon doing this the milling attachment whirred into life. A success.

The artificial phase measured 459 Volt. I did predict it would be high.

So, just the contacter to sort out and a new capacitor to get (from RS) and then I can get on to trying the lathe electrics.

If I could only find my clamp meter I could also check a few currents.

Dave.

Offline Bluechip

  • Madmodder Committee
  • Hero Member
  • *****
  • Posts: 1513
  • Country: england
  • Derbyshire UK
Re: phase convertor
« Reply #38 on: November 02, 2015, 11:31:22 AM »
DavidA:

I have some Ducati motor start caps. marked eg. 12 MFD and they aren't all that old. So, the terminology is not quite obsolete .

I also had some ancient LEMCO & Dubilier silvered mica and waxed paper caps. marked uuF for picofarads and mmF for microfarads.

Slung 'em out some years ago together with anything with 'Hunts' on it ...  :bang:

Dave






I have a few modest talents. Knowing what I'm doing isn't one of them.

Offline DavidA

  • Hero Member
  • *****
  • Posts: 1219
  • Country: gb
Re: phase convertor
« Reply #39 on: December 12, 2015, 01:40:49 PM »
I posted on another thread that today I had a go at getting the Denford to run.

As I have mentioned, I bought this lathe from the company I worked for; but hadn't seen it run for a while.

I first got the EMCO milling attachment running using my capacitor type three phase system. So far so good.

When I connected the lathe to the same system it knocked out the RCD. We are now up to date.

Today I had a look inside the control panel. Lots of unexpected electrics.
It has a DC injection brake system fitted. And I don't know anything about them.

But I don't think I really need to use it. So I will by pass it ; at least for now.

I connected the three phase supply direct to the motor. (after removing the original connections) and tried it. A loud(ish) hum and signs of the motor trying to turn.
Turned it off again and reasoned that this thing hadn't been run for a while and maybe best to disconnect the variable speed belt and just run the motor on it's own; no load.

Try again.  Motor runs slowly with a distinct two - phase growl.

Not a problem as I know that the calculated capacitance for the 2.2 Amp motor is around 16 MFD; and I only had 7 MFD in circuit.

Time to order up those capacitors I referred to earlier.

Then also time to set up the idler motor. That should help it start easier.

Dave.

Offline DavidA

  • Hero Member
  • *****
  • Posts: 1219
  • Country: gb
Re: phase convertor
« Reply #40 on: December 15, 2015, 01:56:26 PM »
Just adding a bit.

The capacitors arrived today (RS overnight post, free)

It was too cold to bother much in the shed today, but I had to just have one 'play'.

I fitted the 10 MFD capacitor.
The motor hesitated briefly then spun up to speed.

The voltages at the motor connection block were

U1 - V1  399 Volt
V1 - W1  445 Volt
W1 - U1  419 Volt

And the currents

U1  0.85 Amp
V1  1.35 Amp
W1 2.42 Amp

Lot's more test to be done yet; both on and off load.

By the way, its a Star connected motor.

Dave.

Offline DavidA

  • Hero Member
  • *****
  • Posts: 1219
  • Country: gb
Re: phase convertor
« Reply #41 on: December 28, 2015, 02:28:54 PM »
Another update.

I now have the motor I acquired connected up as an idler and find it starts easily with 30 MFD attached.  This now feeds my lathe via an isolator switch.

As mentioned before, I did decide that the DC injection braking was only a complication, so spent some time in the shed bypassing all that and have finished up with just the basic control panel, I.E forward, backward and stop.
At the moment I am having a bit of a problem with the contactor controls. I have a fairly good idea of where the problem lay.
Basically the lathe won't start up when I press the go buttons. But if I push in either contactor manually then it runs, but stops as soon as I release. So my contactor solenoids are not powering up.  Tomorrow will be a 'having fun with my test meter' kind of day.

This raises a point for anyone else who may go the same route and use the book.

It gives you very good circuit diagrams , but nothing on connecting up the interlocking switches when you have two contactors. One for forward and one for reverse.  Your on your own with that one.

I suppose that if you were really desperate to get running you could just use one contactor (with overloads) and place a manual change over switch between the overloads and the motor to swap two phases. Thereby getting your reverse.

Dave.

Offline DavidA

  • Hero Member
  • *****
  • Posts: 1219
  • Country: gb
Re: phase convertor
« Reply #42 on: December 29, 2015, 11:59:13 AM »
'It lives, Igor. It lives,'

I took the desperation route and set up the machine using just one contactor and no overloads.

But now I know it works (including the speed control) I can make everything neat and tidy. At the moment the pilot motor is held down to a table with G clamps and the lathe control panel is laying on a wooden chair with all it's innards exposed, Nothing has any covers on. (( need to get at the wiring to measure things). All rather dangerous  :zap:. Re connecting the other contactor will give me  a lathe that actually runs in reverse as well as forward.

I do believe my original problem was down to a disconnection in the contactor relay circuitry. Things quickly start to get complicated when the interlock switches are included.

But the pilot motor / capacitor idea works well. with the lathe running I am getting around 406 Volt average. A small tweak on the capacitance will probably improve that.

As the lathe is the biggest load I am likely to put on the system (and that draws less than 2 AMP), I'm quite satisfied. The only fly in the ointment is that as the transformer is fed from a 16 Amp trip in the house, sometimes the trip drops out on starting the pilot. No big deal as everything is fine once the pilot motor is running. Maybe an additional few MFDs just for starting will improve things.

I'll include some proper reading next time.

Dave :D

Offline Andrew Wildman

  • Full Member
  • ***
  • Posts: 167
  • Country: 00
Re: phase convertor
« Reply #43 on: December 29, 2015, 12:31:42 PM »
Dave, i changed my MCB to a c curve type rather than the standard b type as I had a similar problem with the transformer inrush current.

Offline DavidA

  • Hero Member
  • *****
  • Posts: 1219
  • Country: gb
Re: phase convertor
« Reply #44 on: December 30, 2015, 02:34:51 PM »
Andrew,

I'll probably do the same. It seems to happen only when it is cold.


An update.


I burnt a lot of midnight oil and managed to get the control panel wired up properly.  So it now works as it should. Backward, forward and stop. Only the sud pump to sort out.

So, having got everything running I decided to do a quick test on the threading capabilities.

12 TPI would do.

Chucked up a bit of 1" steel bar. faced it off and took a light skim off the length.  This is the first time the lathe has cut metal for three years.
Next, set up the gearbox.  The 100/127 wheel set and it's banjo are still in a drawer, so the machine is still set up for Imperial.
I followed the instructions. Got to be careful with the Synchro as some operations are done with the machine running, and some are not.

So, spindle, is turning, leadscrew is turning. Close the half-nuts.

Nothing much seems to be happening. But wait, the saddle is moving toward the headstock, but very slowly.

Re check the gearbox settings. all ok.

A look at the reduction gears showed that someone has got then on all wrong. Instead of being a 1:1 gear train fron the spindle to the gear box it is reducing the ratio to 10:1 so I would be cutting something like 120 TPI.
And that is what it looks like.

Ho Hum. Never a dull moment.

Dave.

Offline DavidA

  • Hero Member
  • *****
  • Posts: 1219
  • Country: gb
Re: phase convertor
« Reply #45 on: January 08, 2016, 05:20:56 PM »
Back to the phase convertor theme; well, nearly.

In the book on single to three phase conversion the author also briefly mentions using a three phase squirrel cage motor as a generator. His example has the motor driven by another motor, but a single phase one.

As there seems to be no electrical connection between the two, I assume that the three phase motor (with it's added capacitors) could be driven by, say, a small Diesel engine: or even a steam engine.
You would, of course,  have to set up governor to keep the engine a the required speed as the load changed.

But it has the advantage of having true 120 degree phase shift between all phases.  And with a bit of additional plumbing it could keep your shed warm.

Has anyone tried this ?

Dave.

Offline awemawson

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 8967
  • Country: gb
  • East Sussex, UK
Re: phase convertor
« Reply #46 on: January 08, 2016, 05:25:29 PM »
Three phase electric motors are frequently used in small hydro-electric systems in the third world. I seem to remember that the only modification is capacitors across the three windings

http://www.redrok.com/cimtext.pdf



Andrew Mawson
East Sussex

Offline DavidA

  • Hero Member
  • *****
  • Posts: 1219
  • Country: gb
Re: phase convertor
« Reply #47 on: January 08, 2016, 05:52:09 PM »
Andrew,

Thanks for the links.

Yet something else to add to the 'future project' list.

Dave.